S800 IO using TB840 ramdom fail
We have one Controller PM866 with modules s800 using TB840 and TK811 fiber, the S800 modules fails ramdomly each 2 minutes aprox, the module appears as module missing for 2 or 3 seconds, the indication in hardware appear in red like module is not well plugged . we have 3 racks of modules 36 modules in total and 3 Tb840 and the fails are presented ramdomly in any module of 3 racks.
we change tb840, fiber and CPU, but the problem persist,
Someone have a possible test to do?
or someone have a similar experience and have any solution.
thanks in advance.
we change tb840, fiber and CPU, but the problem persist,
Someone have a possible test to do?
or someone have a similar experience and have any solution.
thanks in advance.
Answers
Hi,
I would strongly recommend you to contact your regional support center for assistance.
I would strongly recommend you to contact your regional support center for assistance.
Problem solved,
fiber optic in wrong position.
fiber optic in wrong position.
1. Check if the optical connectors are plugged in with correct orientation, we had a customer who plugged them in with the locking clips on the wrong side.
2. Read product bulletin 3BSE084764 about a problem with failing cluster modems and check if your components are in the range of effected serial numbers.
2. Read product bulletin 3BSE084764 about a problem with failing cluster modems and check if your components are in the range of effected serial numbers.