how to link process panel 871 and AC500eco pm554 eth
i got process panel 871 (panel 800) and AC500 (pm554 eth) , the coomunication between them is ethernet.
using control builder plus and panel builder version 6, how can i connect the tags from control builder to the hmi ?
using control builder plus and panel builder version 6, how can i connect the tags from control builder to the hmi ?
Answers
Greetings,
There is no direct built-in option to connect tags from Control Builder.
You need to use Modbus TCP communication protocol and define all tags manually.
Please see below similar question:
https://forum-controlsystems.abb.com/396170/Communication-between-AC500-eco-PM5
54-ETH-and-Panel-800-pp877-using-modbus-TCP
There is no direct built-in option to connect tags from Control Builder.
You need to use Modbus TCP communication protocol and define all tags manually.
Please see below similar question:
https://forum-controlsystems.abb.com/396170/Communication-between-AC500-eco-PM5
54-ETH-and-Panel-800-pp877-using-modbus-TCP