Problems after adding I/O card on node
Hello Mr Henkel
We have a Freelance system 2016 SP1 and NO rollups.
After trying to add two cards to one node, the node says configuration error, and gets red in HW structure.
The "old" card seems to work if you look at them for real(diodes)
Could this be a problem which is described in "Freelance 2016 SP1 RU1 release notes"(below in bold)
I cant find the product bulletin described in myABB
No update of PROFIBUS slave parameter after “Load changed objects”. (refer to Product Bulletin 3BDD011838D0323)FRE-930-FW-16S1-001 (PRC 25031)
Best regards
We have a Freelance system 2016 SP1 and NO rollups.
After trying to add two cards to one node, the node says configuration error, and gets red in HW structure.
The "old" card seems to work if you look at them for real(diodes)
Could this be a problem which is described in "Freelance 2016 SP1 RU1 release notes"(below in bold)
I cant find the product bulletin described in myABB
No update of PROFIBUS slave parameter after “Load changed objects”. (refer to Product Bulletin 3BDD011838D0323)FRE-930-FW-16S1-001 (PRC 25031)
Best regards
Answers
Dear Please describe in details what configuration you are using Redundant\Non Redundant, if Redundant please what kind off Remote IOs you are using?
Cheers!
Cheers!
Yes, it could be related. Always install the latest roll-ups. For Freelance 2016SP1 it is RU03! It contains RU01.