VB ERROR : "method '~' of object '~' failed in 3DBADTE369:FACEPLATE :: USERCONTROL_hIDE
control system is 800xA 5.1 REV E , on graphic faceplate of transmitters , one TE showed value of 843 on face plate.
Its RTD in field.
Its Limits are 80 and 90 respectively for HI and HIHI.
But we are not able to find the value 843 in trend as well as tripping alarm also did not occurred.
Also in logic it did not affected.
Its value went to 843 and again after some time it reaches back to normal value.
it happened 2 times.
Please find the related images.



Its RTD in field.
Its Limits are 80 and 90 respectively for HI and HIHI.
But we are not able to find the value 843 in trend as well as tripping alarm also did not occurred.
Also in logic it did not affected.
Its value went to 843 and again after some time it reaches back to normal value.
it happened 2 times.
Please find the related images.



Answers
This question has not yet been answered.
by backdraft
Is this visual basic (vb6) graphics on the Faceplate? I think the error you refer is not related to the overlap on the screenshot you attached, do you agree?
by Tejas.kareliya Rank: 343 on 6/19/2019 12:39:08 AM | Like (0) | Report
hi, that is where I m confused. here is it PG2. our main concern is that transmitter abrupt value show case.
but this event list we get at the same time when this happened.
by backdraft
OK, but the error mentioned 3DBA...:Faceplate, not the Overlap that you have the picture attached, how does the Faceplate look like and was the wrong Value visible there or on the Overlap?