IAC MMS - hardware configuration error - incompatible version primary
Hi Stefan!
could you please advise me what could be the reason for an error of IAC MMS like "hardware configuration error - incompatible version primary"?
There are 2pcs of PM891 and one PM865HI in one project, and only one PM891 in second project. IAC MMS works fine between controllers in one project but controler from the other project has an error like above.
All of IMC MMS have default settings.
Please ask me if you need more details.
Thank you in advance for your time!
Best regards,
MichaĆ
Answers
Not my area of expertise and I don’t see relation with IAC/MMS either.
Check the hardware revision of the processor and CEX modules - the release notes states minimum required hardware revision (PR:A, B C, etc).
Check the hardware revision of the processor and CEX modules - the release notes states minimum required hardware revision (PR:A, B C, etc).
by backdraft
Firmware Version of the PM891 Controller?
by m_lekawski Rank: 4606 on 6/17/2019 10:00:27 PM | Like (0) | Report
Hi,
that's FW891 6.0.200.10
by backdraft
Where do you see this error, on HWUnit 5 under the Controller?