How to setting up ABBCS550 for communication by modbus and RS485 ?
Answers
Hi
to activate the EFB ModBus in ACS550 you need to follow the FW manual instruction. Other group to program:
group 10 for the activation start - stop
group 11 for the speed reference
group 16 for reset and run enable
.....
.....
FW manual instruction, available on:
https://library.e.abb.com/public/313b...
Hope this help you
BR
Flavio
to activate the EFB ModBus in ACS550 you need to follow the FW manual instruction. Other group to program:
group 10 for the activation start - stop
group 11 for the speed reference
group 16 for reset and run enable
.....
.....
FW manual instruction, available on:
https://library.e.abb.com/public/313b...
Hope this help you
BR
Flavio
Source: ACS550 FW MANUAL
Add new comment