Process sectioning in 800xA for Advant master
How to configure the process sectioning in Advant operator station to 800xA for advant
master. Any manual/suggestion appreciated.
Answers
The following manuals might help you:
1) 800xA for Advant Master 6.0 Configuration
2) System 800xA Advant Master Operations 6.0
BR Carsten
The support for Process Section in 800xA is limited, in practice only A/E filtering.
Its a little complicated but it works quite well using absolutely standard 800xA Alarm and Workplace Configuration methods.
The Process Section number is a defined filter on the Alarm and Event list configuration.
To have different Sections on Different Workplaces ( ie like the old Advant station) You need to create One Alarm/Event Configuration Per Advant Station ( or group of Advant Stations that share the same config) and then create one 800xA Workplace Configuration per Alarm/Event Config.
For Each Operator, create a workplace rule that starts the correct Workplace on the required Workstation.
The Process Section number is a defined filter on the Alarm and Event list configuration.
To have different Sections on Different Workplaces ( ie like the old Advant station) You need to create One Alarm/Event Configuration Per Advant Station ( or group of Advant Stations that share the same config) and then create one 800xA Workplace Configuration per Alarm/Event Config.
For Each Operator, create a workplace rule that starts the correct Workplace on the required Workstation.