SV4.1 to SV5.0 SP2 System upgrade MOD300 object problems
We are doing an upgrade of a SV4.1 to SV6.0.3.2 system and a intermediate step is to upgrade at least to SV5.0 Sp2.
I create a SV50 Sp2 system in VM's and have the SV4.1 system from the customer in VM's too.
I made a full backup of the system in SV4.1 as stated in 2PAA113553-600_-_en_System_800xA_4.1_to_5.0_SP2_Upgrade.
I imported the full backup into SV50 Sp2 and except for graphic elements, that we don't care about, everything seems good.
Problem comes with MOD300 objects: MOD_UNIT objects are not imported into Control Structure. In Functional Structure, there are lots of LOOP objects under MOD_UNIT objects that are imported under NO parent into the Functional Structure, all spread out, and MOD_UNIT object do not appear.
Making some test, discovered that making an export of Control Structure without dependencies and then import it into SV50, MOD_UNIT objects are imported but not if the export is done with dependencies. Might be wrong dependencies in this object? How and which ones should I check before import?
My overall question is: is there a procedure to upgrade a 800xA for MOD300 system, some pre-requisites before doing full backup? Should I do the export/import manually between systems?
Thanks for your expertise.
I create a SV50 Sp2 system in VM's and have the SV4.1 system from the customer in VM's too.
I made a full backup of the system in SV4.1 as stated in 2PAA113553-600_-_en_System_800xA_4.1_to_5.0_SP2_Upgrade.
I imported the full backup into SV50 Sp2 and except for graphic elements, that we don't care about, everything seems good.
Problem comes with MOD300 objects: MOD_UNIT objects are not imported into Control Structure. In Functional Structure, there are lots of LOOP objects under MOD_UNIT objects that are imported under NO parent into the Functional Structure, all spread out, and MOD_UNIT object do not appear.
Making some test, discovered that making an export of Control Structure without dependencies and then import it into SV50, MOD_UNIT objects are imported but not if the export is done with dependencies. Might be wrong dependencies in this object? How and which ones should I check before import?
My overall question is: is there a procedure to upgrade a 800xA for MOD300 system, some pre-requisites before doing full backup? Should I do the export/import manually between systems?
Thanks for your expertise.
Answers
Try to run the consistency check in all the structures, before exporting or before doing the FullBackup, maybe a dependency is not consistent and have some not visible errors.
No particular requirements are out of the System 4.1 to 5.0 SP2 Upgrade Manual.
Please let us know your outcome.
by Stefan Stromqvist
Did you load the backup into an empty machine installed with 5.0 SP2, or did you import it into an already existing 5.0 system?
Add new comment