what i need to configure in the PCM600 to communicate by modbus to the PLC?
HI, i want to communicate a REF615 with other REF615 by goose massages but at the same time I need a communication with a PLC (PM573-ETH ) by modbus TCP/IP. the three devices are conected to a switch.
and i would like to know if the communication by IEC61850 affect the modbus comunication.
thanks.
and i would like to know if the communication by IEC61850 affect the modbus comunication.
thanks.
Voted best answer
Hi. you need to configure your relays to communicate with multiple OPC servers. You can use IET600 tool for the same.
2nd. I am not sure whether when 2 relay communicating with each other on Goose can responds to 3rd master on TCP/IP.
Can you please share the configuration drawing for more information.
2nd. I am not sure whether when 2 relay communicating with each other on Goose can responds to 3rd master on TCP/IP.
Can you please share the configuration drawing for more information.
Answers

Hi, first of all thanks to the answer.
Just i need to read a register from the REF615 to the PLC to send by a analog output that signal (but i need to do this while the IEC61850 is betwen both ref615).
i read in the modbus comunication protocol manual that is possible communicate by two protocols simultanusly.
but i do not know if both protocols works in the same port and first work one protocol an then works the other second.
and i don't know what i need to configure in the ref615 to active modbus protocol.