PM867 Hi Controller Fault
Hi
We have two Redundant PM867 Controllers. Firstly Controller -2 (172.16.4.2) and its Backup unit went to Fault. After resetting and downloaded to Controller, and it became running
After sometime Controller -2 (172.16.4.1) and its redundant went to Fault.
Attached the Log files, kindly suggest what might be the problem.
We have two Redundant PM867 Controllers. Firstly Controller -2 (172.16.4.2) and its Backup unit went to Fault. After resetting and downloaded to Controller, and it became running
After sometime Controller -2 (172.16.4.1) and its redundant went to Fault.
Attached the Log files, kindly suggest what might be the problem.
Answers
This question has not yet been answered.
by rahilmohammed Rank: 59 on 5/20/2019 2:54:36 AM | Like (0) | Report
Hi.
"This PM has been automatically restarted.
Reason:
- restarted from an unrecoverable fatal state (Acknowledged)
- System was intentionally shut down"
After resetting and re-downloading does the issue reoccur in both Controller pairs?. Check the cyclic and Total load on the CPU. If total load is very high, reduce load by increasing task cycle time and IO Module bus scan time appropriately.