AC800M opc disconnect after download
I using compact control builder 6.0.2 and its compatible ABB 800 OPC server. after coldrestart download project when i mconnect OPC data access it is not connecting and say some file are missing browse from project directory where i browsed .CTDXML then .CDO and then .CRS file from application folder in project directory. after that OPC connected succcessfully.
Then i saved OPC file and configure as autoload.
after that i done some modification and warm downloaded . i found opc data acess disconnected then again it asking CTDXML then .CDO and then .CRS are missing .
then again i browse these file to connect opc.
i found this problem first time.
Then i saved OPC file and configure as autoload.
after that i done some modification and warm downloaded . i found opc data acess disconnected then again it asking CTDXML then .CDO and then .CRS are missing .
then again i browse these file to connect opc.
i found this problem first time.
Answers
Hi,
Do you have control builder and OPC Server installed in the different nodes (PC's)?
In case yes, after download you have to copy the described files from CBM's node to OPC Server node.
I think, by default, these files are located in the following folder on the node where CBM is installed (from which you are doing download):
C:\ABB Industrial IT Data\Control IT Data\OPC Server for AC 800M\Files
Do you have control builder and OPC Server installed in the different nodes (PC's)?
In case yes, after download you have to copy the described files from CBM's node to OPC Server node.
I think, by default, these files are located in the following folder on the node where CBM is installed (from which you are doing download):
C:\ABB Industrial IT Data\Control IT Data\OPC Server for AC 800M\Files
by gangadhar.gadre Rank: 842 on 6/25/2019 6:22:08 AM | Like (0) | Report
Hello sir,i'm facing the same issue,if u found any solution kindly let me know.