i am facing third party opc communication with 800xa .
i have installed third party opc in same ASCS server and opc is showing runing in matricon explorer,but when i am add this opc through generic opc network so new service create in opc da service.
opc service is showing initialize or undefined.Opc service is in service state.
Please provide any solution.
opc service is showing initialize or undefined.Opc service is in service state.
Please provide any solution.
Answers
I had a similar situation with Cohens Data Hub OPC software. Service started only after PC reboot, but then I couldn't open for edit Cohens Data Hub.
Which software you use to get data from equipment or it's already has an OPC.
If its possible install TopServer or kepware OPC and read data from equipment to OPC and from OPC to ABB.
Which software you use to get data from equipment or it's already has an OPC.
If its possible install TopServer or kepware OPC and read data from equipment to OPC and from OPC to ABB.
The 800xA OPC DA Connector service run as service/background process which is not the same as an OPC client running as a desktop application.
Eg any GUI drawn by OPC server will fail the connection since background processes may not interact with the desktop.
The OPC server must support asynchronous OPC methods.
The service account must permit DCOM callbacks from the OPC server.
Enable the error logs on the OPC DA Connector service in AfwApplogviewer; reason for failure should surface there.
Ask regional ABB for assistance with troubleshooting.
Eg any GUI drawn by OPC server will fail the connection since background processes may not interact with the desktop.
The OPC server must support asynchronous OPC methods.
The service account must permit DCOM callbacks from the OPC server.
Enable the error logs on the OPC DA Connector service in AfwApplogviewer; reason for failure should surface there.
Ask regional ABB for assistance with troubleshooting.
Hi,
In the DCOM identity of the OPC Server you are trying to connect, add the user account from which you are able to read the values in Matrikon. Then try to create Service it will be in service.
In the DCOM identity of the OPC Server you are trying to connect, add the user account from which you are able to read the values in Matrikon. Then try to create Service it will be in service.
In DCOM Identity of the OPC Server you are trying to connect add the User account from which you are able to read values in Matrikon, after this try to enable the service