OPC server for AC800M - Auto load configuration issue
Hello, We have an issue auto load configuration in OPC server for AC800M is not happening after AC800M connectivity server restart. The .cfg files and all .CBCR and .CBD files are available in the location and Enable Auto Load configuration is enabled. If i load manually the cfg file, it is loaded and fine until restart of server.
System version is 800xA v6.0-3
System version is 800xA v6.0-3
Answers
Hi!
From the manual:
From the manual:
There are two common reasons the OPC Server cannot find the files generated by
Control Builder:
1. Wrong Service Account, (no privileges to access aspect directory or Shared network
disk) 800xA or Compact Control Builder respectively.
2. Wrong path to Shared Network disk (Compact Control Builder only).
Regards.