update CP600 HMI Runtime failed. it shows "target device does not have enough free memory. downloading canceled"
my panel builder version is 1.91, the hmi runtime is 1.8. I couldn't download the program until i could update the runtime of the HMI. i deleted all the projects in the HMI. but it still give me the message no enough free memory. how can i do?
Thanks,
Paul
Thanks,
Paul
Answers
Hi Paul
it seems that the size of your HMI program is greater than the panel capacity. What panel model are you using?
The eCo series - CP604-607-610 - has an internal memory of 30 Mb, while the CP600 series has a memory of 256 Mb. Maybe you have used a lot of graphics in your application and this can weigh it down?
To verify that there is not a problem in the panel, you can try to build a small application and check if it is correctly loaded, alternatively maybe you will have to change the panel model.
Hope this help you
BR
Flavio
it seems that the size of your HMI program is greater than the panel capacity. What panel model are you using?
The eCo series - CP604-607-610 - has an internal memory of 30 Mb, while the CP600 series has a memory of 256 Mb. Maybe you have used a lot of graphics in your application and this can weigh it down?
To verify that there is not a problem in the panel, you can try to build a small application and check if it is correctly loaded, alternatively maybe you will have to change the panel model.
Hope this help you
BR
Flavio