CM572 communication with Woodhead SST VME card
I am attempting to connect a CM572 ProfiBus master to a Molex Woodhead SST-PFB3-VME card with the net result of passing information across the VME backplane of the SST card between the AC500 PLC and the other controller in the VME rack.
The SST card can be configured as either a Master or a Slave. In the AC500 PLC, I have imported the GSE file for the slave version of the SST card. For the configuration of the SST card, I need a GSD/GSE file CM572 card. I cannot configure the SST card without a configuration file for the Master ProfiBus device.
The SST card can be configured as either a Master or a Slave. In the AC500 PLC, I have imported the GSE file for the slave version of the SST card. For the configuration of the SST card, I need a GSD/GSE file CM572 card. I cannot configure the SST card without a configuration file for the Master ProfiBus device.
Answers
Greetings,
AFAIK for profibus master devices, there is no GSD/GSE file. These files are only for Slave Devices.
Are you sure, that you need master device file for configuring SST Card?
AFAIK for profibus master devices, there is no GSD/GSE file. These files are only for Slave Devices.
Are you sure, that you need master device file for configuring SST Card?