Change Default Sizing on Web Page Aspect
Hello,
Is there a way to change the default size that a web page aspect opens at? We are using a web server to display alarm rationalization information and it would be nice to open the aspect at a defined size to see the data properly.
800xA SV 5.1 FP4 RevE
Thanks,
Mike
Is there a way to change the default size that a web page aspect opens at? We are using a web server to display alarm rationalization information and it would be nice to open the aspect at a defined size to see the data properly.
800xA SV 5.1 FP4 RevE
Thanks,
Mike
Voted best answer
The sizes are controlled by a "View Class" aspect. Simplest way is to modify the settings in the view class that controls all Web page aspects.
Answers
Thanks Rob. I was able to solve this using a "View Class Reference" aspect on the Web Page, Aspect Category Object. I then changed the setting from "Use Default" to a View Class that I chose and modified. Screenshot is attached.
Mike