datadirect system 800xa add-in
Dear sir,
In the system console, I checked datadirect has been installed well.
However, in excel add-ins, datadirect does not apper...(Nothing found when I look up C: drive with “datadirect” except install files)
Could you help me how to enable it?
Thanks.
Best regards, JS Choi
In the system console, I checked datadirect has been installed well.
However, in excel add-ins, datadirect does not apper...(Nothing found when I look up C: drive with “datadirect” except install files)
Could you help me how to enable it?
Thanks.
Best regards, JS Choi
Voted best answer
Hi,
Follow the Post installation steps as attached to solve this issue.
Follow the Post installation steps as attached to solve this issue.
Answers
• For DataDirect System 800xA: Go to C:\ProgramData\ABB\800xA\DataDirect\Bin and select the file ABBDataDirectSystem800xA.xlam
Reference: 3BUF001094-610 A
Reference: 3BUF001094-610 A
Since the introduction of 800xA version 6.0, there are now two separate Excel toolbar installations for the applications associated with DataDirect. Note the attachment for an explanation of how to add both these Toolbar entries. If these suggestions do not resolve your issue, you should open a Support Case with your local RAC for further analysis.
Regards,
Geof Ledin
Regards,
Geof Ledin
Add new comment