Symphony Plus S+ Operations - Alarm List Problem
Dear Ingo
I am using a Symphony PLUS Operations 2.1 System on a Windows 10 Operating System LTBS 2015.
I'm having problems with the alarms. As for the configuration seemingly OK, I created the lists and alarm:
See print 1
Below the tag configuration
See print 2However when the alarm is active, it does not appear with description and time in the list, it is as if the first column, was very extended, making it impossible to see the others.
See print 3
In short, my alarm lists are not displaying name and description.
Can you help me ?
Best Regard ,

Levi Sampaio

Answers
Dear:
Can you check if on Operating Parameters has the Alarm active?
BR
Can you check if on Operating Parameters has the Alarm active?
BR
Hi,
Can you re-load Balcddeck.xml again and run PGPPostInstallation.exe after shutting down the server.
Can you re-load Balcddeck.xml again and run PGPPostInstallation.exe after shutting down the server.
It may be a little late, but refer to the configuration manual.
2VAA001148-212_B_en_Splus_Operations_2.1_SP2_Operations_configuration_user_manu
al.pdf
Page 152
(Pictured attached)
2VAA001148-212_B_en_Splus_Operations_2.1_SP2_Operations_configuration_user_manu
al.pdf
Page 152
(Pictured attached)
Add new comment