No alarm is generating or working After loading system extension of 800xA Base 5.1-4 (Rev E FP4)
After loading system extension of 800xA Base 5.1-4 (Rev E FP4), Can't able to generate any alarm.
Checked the following
1. Alarm Manager Service & Event Collector service and Configuration.-OK
2. OPC Server- OK
3. Configuration in Logic limits and AE Configuration (Eg. SignalInReal)- OK.
4. OPCDA Connector-OK
Checked the following
1. Alarm Manager Service & Event Collector service and Configuration.-OK
2. OPC Server- OK
3. Configuration in Logic limits and AE Configuration (Eg. SignalInReal)- OK.
4. OPCDA Connector-OK
Answers
Hi,
Check the following
This will give an idea , where will be the problem,
BR
ATP
Check the following
- Check that the alarm manager has an active subscription by using applog
- Check activated events collector logs in applog.
This will give an idea , where will be the problem,
BR
ATP
OK, so what were you really trying to do ? - You would not normally add the "System Base" feature to a running system.
Was this a new installation or an upgrade ?
Do the System Alarms, Soft Alarms, Alarm Expressions etc work ?
Have you tried a third party AE client to see if the AC800M OPC AE Server and 800xA AE servers are working ?
Did the upgrade include changes to the AC800M software and firmware ? Did you load the changes to the Controllers ?
Was this a new installation or an upgrade ?
Do the System Alarms, Soft Alarms, Alarm Expressions etc work ?
Have you tried a third party AE client to see if the AC800M OPC AE Server and 800xA AE servers are working ?
Did the upgrade include changes to the AC800M software and firmware ? Did you load the changes to the Controllers ?
by ranjith.newton Rank: 398 on 4/16/2019 3:27:15 AM | Like (0) | Report
Alarm is working without this 800xA Base 5.1-4 extension load
by ATP
What about Event collector?
by ranjith.newton Rank: 398 on 4/16/2019 3:53:07 AM | Like (0) | Report
Checked. AE Server is OPC AE Server for AC800M is configured. and also in service state.