Prevent ACS880 direction change in local mode
Dear all,
Is there any way to prevent the operator from changing the direction in local mode in ACS880 VFD?
Thanks in advance.
Is there any way to prevent the operator from changing the direction in local mode in ACS880 VFD?
Thanks in advance.
Voted best answer
Hi,
Try with:
Negative speed reference enable 20.24=0
or
Minimum speed 30.11 = 0
I'm not quite sure if these will work in local mode
Try with:
Negative speed reference enable 20.24=0
or
Minimum speed 30.11 = 0
I'm not quite sure if these will work in local mode
Source: 3AUA0000085967
by ayoung Rank: 9586 on 6/21/2019 9:04:29 AM | Like (1) | Report
did you figure this out yet?
by AbdelrazzaqHiasat Rank: 192 on 6/25/2019 3:48:59 AM | Like (0) | Report
Negative speed reference enable 20.24=0 solved the issue,
Also, you can disable the local mode
Add new comment