AC800M communication with Conzerve meters on Modbus
sir,
it em6433
it em6433
Voted best answer
Please check the start address format. Also you have to give 1 register less value to read the parameter. for example- frequency is in register 3110 (32bit data), then in control builder you have to read 3109 register.
Answers
Hi,
Please find the below link for Modbus Address registers for EM6400 series MFM.
https://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/l
ive/FAQS/345000/FA345958/en_US/EM%206433%20series%20Communication.pdf
Please find the below link for Modbus Address registers for EM6400 series MFM.
https://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/l
ive/FAQS/345000/FA345958/en_US/EM%206433%20series%20Communication.pdf