High Speed signals per IO bus
Hi,
I am using one DC-532 and five DI524 with PM583-eth controller on IO bus (directly connected with controller), where I am using 2 high speed channels of each module.
Is it correct to connect 12 High speed signals (8-10 counts / second) in this way.
Thanks in advance.
I am using one DC-532 and five DI524 with PM583-eth controller on IO bus (directly connected with controller), where I am using 2 high speed channels of each module.
Is it correct to connect 12 High speed signals (8-10 counts / second) in this way.
Thanks in advance.
Voted best answer
Hi,
I think you can use that configuration, for the described task.
Please look in the help for the possible types of counters in case each input channel is used for own counter.
E.g. you can't use "One up-counter with enable input" which requires 2 fast counting inputs.
I think you can use that configuration, for the described task.
Please look in the help for the possible types of counters in case each input channel is used for own counter.
E.g. you can't use "One up-counter with enable input" which requires 2 fast counting inputs.