I have a S7-1200 plc acting as a Master to 5 nos of ci867 as slave.What are the port numbers available for modbus for ci867.Can i use 502 for all 5 plc or use 502-506 respectively.
I have a S7-1200 plc acting as a Master to 5 nos of ci867 as slave.What are the port numbers available for modbus for ci867.Can i use 502 for all 5 plc or use 502-506 respectively.
Answers
Yes, you can use port 502 on all. 502 is the standard Modbus TCP port for most devices.
The IP address however must be different on all Ci867.
The IP address however must be different on all Ci867.
Hi,
Port no. 502 is fixed for CI867 Modbus TCP/IP communication. It can not be changed.
Regards,
Parthi
Port no. 502 is fixed for CI867 Modbus TCP/IP communication. It can not be changed.
Regards,
Parthi
Hi,
Port no. 502 is fixed for CI867 Modbus TCP/IP communication. It can not be changed or configurable by user.
Regards,
Parthi
Port no. 502 is fixed for CI867 Modbus TCP/IP communication. It can not be changed or configurable by user.