AC800M Controller accessed by Multiple Compact HMI
Is it possible to have one AC800M Controller talking to 3 Compact HMI ?
Answers
Hi,
It is Possible as long as Maximum 3 OPC DA/AE subscribers per controller can be maintained.If redundant connectivity servers are used then no. You might have to look at option of using OPC surrogate server to read data from one CHMI to another using Generic OPC Client or PLC Connect connectivity.
Please check the answer in the below link.
https://forum-controlsystems.abb.com/...
Regards
Rahil
It is Possible as long as Maximum 3 OPC DA/AE subscribers per controller can be maintained.If redundant connectivity servers are used then no. You might have to look at option of using OPC surrogate server to read data from one CHMI to another using Generic OPC Client or PLC Connect connectivity.
Please check the answer in the below link.
https://forum-controlsystems.abb.com/...