I get "wrong module type" after trying to add an AI815 module to my PM861 controller. See attached screenshot. Controller log says: "W 2019-03-25 15:41:01.605 at position 1 found DO993, expected AI815".
My setup is:
PM861
TU810
800xA 5.1 fp 4
S800IoMOdulebusHwLib 1.3-2
Whats the problem? Faulty AI815 card?
My setup is:
PM861
TU810
800xA 5.1 fp 4
S800IoMOdulebusHwLib 1.3-2
Whats the problem? Faulty AI815 card?
Answers
Hi,
Check if AI815 is locked to TU810 (hardware switch) and if TU810 is correctly connected to the CPU.
Check if the 24VDC power supply is correctly connected to TU810 or set External Power Supervision = false
In case it is an empty controller, try to do download with cold restarart option or cold restart the CPU (remove backup battery and cycle the power supply).
Check if AI815 is locked to TU810 (hardware switch) and if TU810 is correctly connected to the CPU.
Check if the 24VDC power supply is correctly connected to TU810 or set External Power Supervision = false
In case it is an empty controller, try to do download with cold restarart option or cold restart the CPU (remove backup battery and cycle the power supply).