Configure Alarm Shelving in 800xA based on alarm priorities
Hi all,
Is it possible to configure Alarm Shelving in 800xA in the way, that only alarms with certain priorities can be shelved?
For example, Alarms with priority 1 cannot be shelved but alarms with priority 2 or higher can be shelved.
According to the documentation I could not find this option, does anybody know?
Thanks in advance and Best Regards,
Daniel
Is it possible to configure Alarm Shelving in 800xA in the way, that only alarms with certain priorities can be shelved?
For example, Alarms with priority 1 cannot be shelved but alarms with priority 2 or higher can be shelved.
According to the documentation I could not find this option, does anybody know?
Thanks in advance and Best Regards,
Daniel
Answers
Permissions are defined on node, user & object level. If the operator has the shelving permission for a particular object (while working from a particular node), he/she can shelve any alarm on that object.
I suggest that you speak with your regional ABB sales representative about enhancement requests, or customer funded development (which may be an alternative, if the function is dearly required).
I suggest that you speak with your regional ABB sales representative about enhancement requests, or customer funded development (which may be an alternative, if the function is dearly required).