redundant pair NI21/NPM22 is continuously restarting.
dear sirs, We have two pairs NIS21/NPM22 an two redundant BRC410. when connect the primary pair NIS21/NPM22 and the BRC the system work fine. When whe insert de secondary pair NIS21/NPM22 this start to continuosly restart.
https://youtu.be/a17eOluARxA
Can you giv us a clue?
https://youtu.be/a17eOluARxA
Can you giv us a clue?
Answers
There are no redundancy cable installed between the NPM22 modules.
The backup module can't copy configuration from primary due to the missing cable, thus its failing to go into "hot backup ready" state and a reset is issued instead.
Install a PMKHRMBRC3000A cable between them and it should fix the issue.
The backup module can't copy configuration from primary due to the missing cable, thus its failing to go into "hot backup ready" state and a reset is issued instead.
Install a PMKHRMBRC3000A cable between them and it should fix the issue.