RTA Board Config won't start from Control Structure - 800xA SV6.0.3
We have an 800xA SV6.0.3 system, where we are not able to start RTA Board Config nor Online Builder
When trying to start RTA Board Config from the Control Structure it fails...

When trying to start the Online Builder directly, it reports No defualt node available...

When trying to do RTA Board Backup it fails.

CBA ONB 3.2/0 is installed...

Besides the RTA Board Config issue, the PU410 RTA board works fine.
# Data from Advants Controllers are being provide to the system.
# The PU410 RTA Board is listed in the RNRP monitor with both IP address.
Any suggestions on how to fix this issue with starting RTA Board Config ?
Regs.
Stephan
When trying to start RTA Board Config from the Control Structure it fails...

When trying to start the Online Builder directly, it reports No defualt node available...

When trying to do RTA Board Backup it fails.

CBA ONB 3.2/0 is installed...

Besides the RTA Board Config issue, the PU410 RTA board works fine.
# Data from Advants Controllers are being provide to the system.
# The PU410 RTA Board is listed in the RNRP monitor with both IP address.
Any suggestions on how to fix this issue with starting RTA Board Config ?
Regs.
Stephan
Answers
RTA Board Configuration should only work on the Connectivity servers. You cant start / stop / modify the RTA board on other nodes.
Installing the RTA drivers on a Connectivity Server automatically installs On Line Builder and configures one Node for the local RTA board.
- Is your problem happening on the Connectivity Servers ?
- Did you try to install a Complete Control Builder A ( ie APB, FCB, ONB etc ) onto this Connectivity Server ?
Installing the RTA drivers on a Connectivity Server automatically installs On Line Builder and configures one Node for the local RTA board.
- Is your problem happening on the Connectivity Servers ?
- Did you try to install a Complete Control Builder A ( ie APB, FCB, ONB etc ) onto this Connectivity Server ?
Hello
I assume that this is on the CS server.
Something must have went wrong during the installation.
I recommend you to do maintenance stop on the server and un install AC400 connect , ( under programs and features) and install it again manually to repair the function.
The RTA board maintenance function , (Sub set of a complete Online Builder) do not have support for projects and controller nodes, it's only to maintain the RTA.
Best Regards
Jan-Erik
I assume that this is on the CS server.
Something must have went wrong during the installation.
I recommend you to do maintenance stop on the server and un install AC400 connect , ( under programs and features) and install it again manually to repair the function.
The RTA board maintenance function , (Sub set of a complete Online Builder) do not have support for projects and controller nodes, it's only to maintain the RTA.
Best Regards
Jan-Erik
Thx for your reply's..
Yes, I'm aware of that the RTA board Config can only be started on the actual CS server, but still this is failing...
Next week when I'm back in the office, I'll to re-install AC400 connect... And yes System Configuration Tool is three steps for us engineers :-)
Yes, I'm aware of that the RTA board Config can only be started on the actual CS server, but still this is failing...
Next week when I'm back in the office, I'll to re-install AC400 connect... And yes System Configuration Tool is three steps for us engineers :-)