Modbus TCP Connection Down -7001
Answers
This problem can also occurs, while You are not only one master reading slave device at the same time. Try to extend watchdog for it.
Another issue is that, You writing block is wrongly connected - You will only write once in Yours case. Request needs to be pulsed by logic (write only when detected rising edge on input)
Another issue is that, You writing block is wrongly connected - You will only write once in Yours case. Request needs to be pulsed by logic (write only when detected rising edge on input)
by Fredrik Rank: 580 on 3/13/2019 12:35:02 AM | Like (0) | Report
There is a known bug in v6 which causes a similar error. Are you using the latest version of CI867ModbusTcpHwLib?
by umut.ergin Rank: 1613 on 3/13/2019 12:50:23 AM | Like (0) | Report
I am using CI867ModbusTcpHwLib 2.11-4