hello,
Is there any ddcs communication module for AC500 to ACS600 multi drive.
Is there any ddcs communication module for AC500 to ACS600 multi drive.
Answers
Greetings,
Please see below manual for ACS600 Multi Drive Systems:
https://library.e.abb.com/public/e73a...
On Section Appendix-C indicates the Fieldbus Adapter for ACS600.
You can use embeded Modbus RTU with your AC500 PLC System.
Hope it helps.
Please see below manual for ACS600 Multi Drive Systems:
https://library.e.abb.com/public/e73a...
On Section Appendix-C indicates the Fieldbus Adapter for ACS600.
You can use embeded Modbus RTU with your AC500 PLC System.
Hope it helps.
Hello, there is module PE1364E from Swedish company Processelektronik, which works as slave on Profibus and DDCS master able to talk with 5 drives. I don't have experience with this module, but with other type PE1376 that was working fine. Also designer and developer of the module gave my excellent support that was very helpful during commissioning.
Maybe range of Processelektronik modules can be delivered directly by ABB.
Maybe range of Processelektronik modules can be delivered directly by ABB.