Licensing Two IMS Server for 800XA 6.0.2
We have two IMS server , to have parallel log to make IMS server redundancy.
Project we have 5000 Tags to be logged
We bought 5000 Dual log license -> will this satisfy the total license requirement of IMS , or do i need to buy 10000 Dual logs ?
Project we have 5000 Tags to be logged
We bought 5000 Dual log license -> will this satisfy the total license requirement of IMS , or do i need to buy 10000 Dual logs ?
Answers
A 5,000 Dual Log License will be enough. A 'Dual Log' allows you to have twice as many logs as the number of Dual Logs. That means that a 5,000 Dual Log license allows you 10,000 logs. With two IM:s where you configure the log templates with logs in both IM:s and you configure 5,000 instances of this (these) log template(s), 5,000 licences will be used by each IM, so you are OK.
Hi,
Yes 5000 Dual log license is enough to meet your requirement. 5000 Property logs can be logged in dual IMS Server.
If you have one tag -> 1 property to be logged then 5000 Dual Log license is enough.
If you have one tag -> 2 properties to be logged then 5000*2=10000 Dual logs license is required.
Regards,
Sri
Yes 5000 Dual log license is enough to meet your requirement. 5000 Property logs can be logged in dual IMS Server.
If you have one tag -> 1 property to be logged then 5000 Dual Log license is enough.
If you have one tag -> 2 properties to be logged then 5000*2=10000 Dual logs license is required.
Regards,
Sri