Need configuration settings for Modbus in S+ Operations 2.0.4
Answers
out_ad2 -->40991 need to be changed to 990 and try out. If not, 991 based on the 3rd party device address (starts from 0 or 1).
out_ad5 -->value should be 1
out_txt1 --> not sure, if it is really required. Try removing it, if the above setting is not working.
The details about the configuration is available in chapter 9 of Scanner reference guide.
out_ad5 -->value should be 1
out_txt1 --> not sure, if it is really required. Try removing it, if the above setting is not working.
The details about the configuration is available in chapter 9 of Scanner reference guide.
Source: S+ Operations Scanner Reference Guide