Safeguard 400 decomissioning
Hi guys,
I have a trivial question. I have to decomission/delete an existing Dual Safeguard 400 controller from the 800xA v5.1. Other AC450/Safeguard 400 controllers are still active in 800xA and will remain active. So I suppose I only have to delete only delete the selected Safeguard controller from control structure, and that's it?
Thanks in advance,
Hrvoje
I have a trivial question. I have to decomission/delete an existing Dual Safeguard 400 controller from the 800xA v5.1. Other AC450/Safeguard 400 controllers are still active in 800xA and will remain active. So I suppose I only have to delete only delete the selected Safeguard controller from control structure, and that's it?
Thanks in advance,
Hrvoje
Voted best answer
Hello.
If you have removed a Safeguard controller you simply remove the node object and everything uploaded below in the control structure.
You may also remove the net and node number for the NODE_DESCR DB element on the RTA board for this pair of Safeguard nodes, to clean up the system.
Else, if the Safeguard node numbers are re used nodes will be treated as a Safeguard by 800xA.
The NODE DESCR element configuration is described in manual 800xA for Safeguard, 3BNP004848-600
Best Regards
Jan-Erik
If you have removed a Safeguard controller you simply remove the node object and everything uploaded below in the control structure.
You may also remove the net and node number for the NODE_DESCR DB element on the RTA board for this pair of Safeguard nodes, to clean up the system.
Else, if the Safeguard node numbers are re used nodes will be treated as a Safeguard by 800xA.
The NODE DESCR element configuration is described in manual 800xA for Safeguard, 3BNP004848-600
Best Regards
Jan-Erik