Rack redundancy Ac460 controller
Hi,
Is there any loop configuration for Rack Redundancy in AC460 controller using DSBC 173?
What are the pre- requisite to make rack redundant?
Thanks
Answers
No loop configuration for Rack S100 redundancy, it's first a hardware structure redundant (connection unit DSTA001 or DTTX180) and configure the I/O rack with redundancy.
Hi, I'm curious your requirement for rack redundancy as normally the power supply is redundant (bulk and 5V regulators), the AC460 CPU has 1:1 redundancy ,the I/O LAN has redundancy and of course you can have dual instruments. As the rack has no active devices e.g capacitors/chips, you can argue that failure is very unlikely of the rack.
Regards,
Matt
Regards,
Matt