How to remove AC800M OPC Server Name appearing in Alarm band on compact hmi v6.0.3
we tried to remove the OPC source name for each signals on control structure but this error appears again
Answers
Hi,
Goto Particular Alarm List --> Right Click Config View --> Open --> Goto Columns --> In Message Fields , option to select the column name to be appear in the alarm list.
Check this one.
Goto Particular Alarm List --> Right Click Config View --> Open --> Goto Columns --> In Message Fields , option to select the column name to be appear in the alarm list.
Check this one.
Please provide a screen shot of the alarm's "Event Details..." (right click the alarm and select the command from the context menu).
Finally, you may opt to display the SrcName and/or ObjectName columns in your alarm and event lists.
- SrcName = defined by program downloaded to the controller.
- ObjectName = defined by HMI after looking up the alarm's SourceGUID.
Finally, you may opt to display the SrcName and/or ObjectName columns in your alarm and event lists.
by kstoilov
Hi,
Can you send a picture or explanation how do you created/configured your alarms