Hi
I have two workplaces with two different alarmlists.
Alarmlist 1 contains alarms with class 3.
Alarmlist 2 contains alarms with class 4 and 5.
Controlroom 1 has a workstation with alarmlist 1 (class 3).
Controlroom 2 has 2 workstations one with alarmlist 1 (class 3), and one with alarmlist 2 (class 4 and 5).
Controlroom 1 is manned between 0600 - 1600
when the controlroom 1 is manned i would like to silence alarmlist 1 in the controlroom 2
Can i automate this?
I would also like to be able to add class 3 to alamlist 2 so it shows alarms with class 3, 4 and 5. between 1600 -0600.
Can i automate this?
Best regards /anders
Voted best answer
PoC may work; but I cannot tell if the taking/releasing responsibility can be automated the way you need.
Answers
Hi!
Point-of-Control functionality could be worth looking into. Downside is that it requires a license...
BR
Point-of-Control functionality could be worth looking into. Downside is that it requires a license...
BR
by anders.alm Rank: 743 on 2/19/2019 5:15:04 AM | Like (0) | Report
OK i have to solve it another way, thanks for quick response