AF100 - S800 configuration of ISP/OSP values
Hi.
We have used an AC400 controller with AF100 and S800 IO cards (CI810 interface). How can i configure the ISP values for digital input cards and OSP values for digital output cards ?
Best Regards
We have used an AC400 controller with AF100 and S800 IO cards (CI810 interface). How can i configure the ISP values for digital input cards and OSP values for digital output cards ?
Best Regards
Voted best answer
Its all in the DB element manuals. For AC400 controllers ...
- For AIS .... Modify the Settings of the ERR_CTRL and ERR_VAL terminals

- For AOS modify the settings of OSP_CTRL and OSP_VAL

- For DIS .... ERR_CTRL

- For DOS .... OSP_CTRL and OSP_VAL

- For AIS .... Modify the Settings of the ERR_CTRL and ERR_VAL terminals
- For AOS modify the settings of OSP_CTRL and OSP_VAL
- For DIS .... ERR_CTRL
- For DOS .... OSP_CTRL and OSP_VAL
Answers
The ISP is used to avoid unnecessary signals and if communication fails between the controller and io module disconn then the application variables set to predetermined which means that we assigned manually. To configure ISP (Input set to predetermined) select the IO module and go to the settings tab> select the ISP control channel then two options are available
1)keep current value : this will take the last default value from the IO module
2)set ISP value : To set the predefined value to the input io module when the communication failure.
select the Set ISP value to define the value and and give the value at the ISP value channel.
1)keep current value : this will take the last default value from the IO module
2)set ISP value : To set the predefined value to the input io module when the communication failure.
select the Set ISP value to define the value and and give the value at the ISP value channel.
Dear,
OSP (output set as predetermined ) is used to the predefined value to certain channel in the certain output module when the cable disconnected between the controller and IO Device and power failures of the controller.
To set OSP go to the particular io module >right click on it>select the editor>go to the OSP control channel choose the OSP value to consider predefine value and give the predefine value at the OSP value channel(true or false).
Keep current value explained in earlier answer.
Please refer the below attached file for reference.
OSP (output set as predetermined ) is used to the predefined value to certain channel in the certain output module when the cable disconnected between the controller and IO Device and power failures of the controller.
To set OSP go to the particular io module >right click on it>select the editor>go to the OSP control channel choose the OSP value to consider predefine value and give the predefine value at the OSP value channel(true or false).
Keep current value explained in earlier answer.
Please refer the below attached file for reference.
Add new comment