Dear sir if LD(linking device) is defective.please tellme Changing procedure
if LD(linking device) is defective.please tellme Changing procedure
Answers
Hi,
You can look in the net for documents or in help files. For example look in the document 3BDD011677-600 A.
You can look in the net for documents or in help files. For example look in the document 3BDD011677-600 A.
Source: 3BDD011677-600 A
Hi,
Not much to do in LD800HSE replacement. Will be easy if you have redundant LD configuration.
Configure IP in New LD. Default IP is 192.168.1.20
refer manual https://library.e.abb.com/public/cef8...
Not much to do in LD800HSE replacement. Will be easy if you have redundant LD configuration.
Configure IP in New LD. Default IP is 192.168.1.20
refer manual https://library.e.abb.com/public/cef8...
As it is IP configured, Need to note down existing IP details with Sub net mask.
Then replace with new one and Through configuration port, assign the required IP and subnet mask.
Follow the procedure as per given in Doc:3BDD011677-600.
From page no:47
Then replace with new one and Through configuration port, assign the required IP and subnet mask.
Follow the procedure as per given in Doc:3BDD011677-600.
From page no:47