Control Structure aspect not made in IEC61850 Functional Structure upload
Hi all
We are communicating with some relays with IEC61850 via the IEC61850 OPC server Communication Engineering Tool (CET) to 800xA. In CET we are defining the alarm severity and description of some of the signals.
As far as I'm aware of, these alarms "comes into" 800xA through the Functional Structure. In each Conducting Equipment and Logical Node under the Functional Structure, there is normally a Control Structure Aspect that points to the object placed under Control Structure in the Engineering Workplace.
All this is usually made automatically when using the IEC61850Uploader.
Though in this new project, where we are using IEC61850 version 6.0.3-1 (Build 6.0.58070.24356), the Control Structure Aspect is not made for the Logical Node objects under Functional Structure. This means that the alarm severity and alarm description is not pointed towards the object in the control structure, and does therefore not come under it's specific object, e.g. the Bay module.
This Control Structure aspect is made for Substation, Voltage Level, Bay and Conducting Equipment, but not for the Logical Nodes.
Due to this, I can also see under the Control Connection aspect for a Logical Node in the Functional Structure, that the value is "AddItem Error". If I then manually is inserting a Control Structure Aspect pointing at the Control Structure, the value shows the correct value. Therefore I can do this manually, but I would prefer not (we have a lot of alarms coming from IEC61850, and this have to be done after every new upload).
Have anybody experienced this kind of problem before or know a solution?
In advance, thanks a lot for your answers.