I connected Acs 800 to AC800M Via profibus option module and make all the configuration but it doesn't work
Answers
Hi,
Possible reasons may be,
1.Check Profibus looping (End Resistance,Cable arrangement)
2.Check in VFD drive whether the profibus communication is enabled.
Possible reasons may be,
1.Check Profibus looping (End Resistance,Cable arrangement)
2.Check in VFD drive whether the profibus communication is enabled.
Greetings,
First of all I did not understand why you need to import GSD file of RPBA-01, it is already exist in Control Builder Library, and you can use use.
By the way, could you please share the RPBA-01 LED status with us?
Hope it helps you.
First of all I did not understand why you need to import GSD file of RPBA-01, it is already exist in Control Builder Library, and you can use use.
By the way, could you please share the RPBA-01 LED status with us?
Hope it helps you.
You can also use a web browser towards your controller, just go to http://<IP-address>/ and log in to the CI854 module.
There is a choice called Live List there that shows nodes that can be seen on the profibus.
There is a choice called Live List there that shows nodes that can be seen on the profibus.