variador acs880
Goodnight .
I am writing to you because of a problem I have with the 880 inverter, I already integrate it with dcs 800x.a, check the parameters in the inverter and apparently everything is fine, I can send feedback to the inverter and I see it on the inverter screen but when I send it the command to be through the face plate does not start, I see that in one of your answers you mention that for the start and stop, the control word has a precise bit within the set a1 to get the desired function, could you give me more detail about that, I forgot to say that the communication is via profibus dp. I thank you in advance for your answer.
Voted best answer
Hi
in addition to the link of my old answer, to try to solve the issue you need to verify:
to have correctly set the drive parameters to operate with profibus
to give via DCS the correct command - control word - to the drive, generally you can try one Variable directed MOVE to the control word.
The most diffuses commands are (decimal format) - 1150 to stop the drive, 1151 to start the drive, 1143 to stop in ramp the drive, 1152 per reset del drive
Hope this help you
in addition to the link of my old answer, to try to solve the issue you need to verify:
to have correctly set the drive parameters to operate with profibus
to give via DCS the correct command - control word - to the drive, generally you can try one Variable directed MOVE to the control word.
The most diffuses commands are (decimal format) - 1150 to stop the drive, 1151 to start the drive, 1143 to stop in ramp the drive, 1152 per reset del drive
Hope this help you