Unable to operate valve object from faceplate
Hii,
We are using SIS PM865 Controller and project with SIL level "SIL 1-2 " we have created new valve object for which buttons on faceplate were not getting highlighted leading to restrict the operation like auto manual and open close.
we had checked the SIL Acess in Plant explorer for same object which resembling with old object.
Can any let me known how to resolve the issue
attaching the screen shot of the same
We are using SIS PM865 Controller and project with SIL level "SIL 1-2 " we have created new valve object for which buttons on faceplate were not getting highlighted leading to restrict the operation like auto manual and open close.
we had checked the SIL Acess in Plant explorer for same object which resembling with old object.
Can any let me known how to resolve the issue
attaching the screen shot of the same
Answers
go to Object Type Structure and open the Config View of the faceplate. Under Buttons you can see what enable your button:

/Erik
/Erik
Problem rectified by following steps
Plant explorer < Control Structure < Application< Aspects -(Application) < SIL Access< Select valve Object
in that Access level to be changed from read only to Confirm
Note: while modifying , project should be opened in control builder than download the program
Plant explorer < Control Structure < Application< Aspects -(Application) < SIL Access< Select valve Object
in that Access level to be changed from read only to Confirm
Note: while modifying , project should be opened in control builder than download the program
by Deepak.S Rank: 17 on 1/30/2019 12:17:14 AM | Like (0) | Report
please attach the error screen shot.
Add new comment