Use of the same domain server for System 6.0.3 and System 5.1 FP4
Hello,
We want to use the same domain server for two Systems, one is version 6.0.3 and the other is version 5.1 FP4. We would like to know if both System can work in the same physical server and which Windows version does it require.
We want to use the same domain server for two Systems, one is version 6.0.3 and the other is version 5.1 FP4. We would like to know if both System can work in the same physical server and which Windows version does it require.
Answers
This should not be a problem as the DC is the Security server. The only issue would be the use of RNRP on the DC. As there are 2 800xA systems there may also be an issue with the automatic loading of the 6.x nodes, as it may see both nodes at the sametime...If you wish to have this setup I would suggest that your network arrangements ensure that either 800xA system cannot communicate with the other in any way, except the DC's. This should ensure no problems.
Hello,
As per manual xA5.1 supports for windows 2008 R2 server and xA6.0.3 supports for windows 2012 R2 server.
But using the same domain for domain security is not an issue as long as network areas are different but RNRP in the domain should be compatible windows platform.
you can use either windows 2008 r2 or windows 2012 r2 in the domain server.
but keep in mind that AC800M doesn't talk to both OPC server of the different platform
As per manual xA5.1 supports for windows 2008 R2 server and xA6.0.3 supports for windows 2012 R2 server.
But using the same domain for domain security is not an issue as long as network areas are different but RNRP in the domain should be compatible windows platform.
you can use either windows 2008 r2 or windows 2012 r2 in the domain server.
but keep in mind that AC800M doesn't talk to both OPC server of the different platform