problem with log in PM554-TP-ETH
Hi,
i can't loggin to PM554-tp-eth CPU no more after i changed its ip address. If i do a scan with ip configuration i can see the cpu with all the correct parameter. I set communication setting directly with the scan, but when i try to log in the programm show me always communication error's pop up and i can't see no more the communication parameter in the online menu in codesys.
After i changed ip address, led status on cpu is in this condition: led power green, led run blinking, led error red and for all this procedure i put the cpu in stop mode with its switch.
Where am I doing wrong?
Thanks
i can't loggin to PM554-tp-eth CPU no more after i changed its ip address. If i do a scan with ip configuration i can see the cpu with all the correct parameter. I set communication setting directly with the scan, but when i try to log in the programm show me always communication error's pop up and i can't see no more the communication parameter in the online menu in codesys.
After i changed ip address, led status on cpu is in this condition: led power green, led run blinking, led error red and for all this procedure i put the cpu in stop mode with its switch.
Where am I doing wrong?
Thanks
Voted best answer
Hi
changes to the IP address must be made with the CPU in STOP, for security reasons.
Do not forget after the IP modification with SCAN utility, modify the address in Automation Builder setup and last but not least, after the re-load in to the CPU, create a boot project in Codesys session.
Hope this help you
changes to the IP address must be made with the CPU in STOP, for security reasons.
Do not forget after the IP modification with SCAN utility, modify the address in Automation Builder setup and last but not least, after the re-load in to the CPU, create a boot project in Codesys session.
Hope this help you
Answers
Hi,
I have the same problem. The CPU and my laptop are well configured but when i open codesys via the "application" feature in automation builder, the communication parameter in codesys is missing as well..
I have the same problem. The CPU and my laptop are well configured but when i open codesys via the "application" feature in automation builder, the communication parameter in codesys is missing as well..
Just for information i fixed the problem.
The issu was: when i changed ip address to CPU, from 192.168.6.X to 192.168.14.X, i had also to add to my pc ip settings the new line 14 that i set for the plc (see attachment)

See also this guide:
https://library.e.abb.com/public/4c8a...
Hope it can be helpfull
The issu was: when i changed ip address to CPU, from 192.168.6.X to 192.168.14.X, i had also to add to my pc ip settings the new line 14 that i set for the plc (see attachment)

See also this guide:
https://library.e.abb.com/public/4c8a...
Hope it can be helpfull