ACS 355 has 0035 fault code how do i fix it i tried disabling parameter 3023 it didnt work
it was running a submersible pump and its suspected it was struck by lightning
Answers
Hi
the fault code 35 means - from the manual - that the input power cables have been inverted with those of the motor.
Since I assume that this fault was not there before, I'm afraid you're right and that as a result, due to the lightning, you'll have to change the drive.
You can made one simple, last test: try to connect only the power to the drive and verify if the fault code appear every time, and next if the fault code not appear try to connect one different motor.
I understand that it looks like a stupid test, but this allows you to understand if there is dependence between the effects of lightning only on the drive, only on the electrical motor, or both
Hope this help you
the fault code 35 means - from the manual - that the input power cables have been inverted with those of the motor.
Since I assume that this fault was not there before, I'm afraid you're right and that as a result, due to the lightning, you'll have to change the drive.
You can made one simple, last test: try to connect only the power to the drive and verify if the fault code appear every time, and next if the fault code not appear try to connect one different motor.
I understand that it looks like a stupid test, but this allows you to understand if there is dependence between the effects of lightning only on the drive, only on the electrical motor, or both
Hope this help you