What is the maximum length of TK850 cable ?
We have a requirement to CI853 card to existing cable, due to space constrains I need to use TK850 ( CEX-Bus Extension cable) , as per standard the cable length is 0.7 meters, Is it possible to use higher length or is this cable is customisable ?
Voted best answer
Hi,
AFAIK TK850 can not be customized and it is a standard factory produced cable with 0,7 m length, it is not allowed to extend it.
Is that a single or redundant processor, is that PM86x processor or PM891, do you have BC810?
Look for possible use of BC810 as well (if you don't have such)
AFAIK TK850 can not be customized and it is a standard factory produced cable with 0,7 m length, it is not allowed to extend it.
"Only one TK850 CEX-Bus extension cable may be used in any one CEX-Bus. Cable length: 0.7 m (2.3 ft)."
What is your existing configuration and where do you want to add CI853?Is that a single or redundant processor, is that PM86x processor or PM891, do you have BC810?
Look for possible use of BC810 as well (if you don't have such)
Source: 3BSE036351-510 A
Add new comment