Alarm conditions on Each Function Block can't be Activated?
Dear Expert,
I've been struggling to configure the alarm on 800xa System. System using 800xa Ver 6.0.2, controller using PM862, operating system using windows 10, system architecture just use 2 pc, 1 for EWS act as Engineering workstation, Aspect Server and Connectivity Server, second PC use for Operator works station. We already configure the Alarm Manager, Even Collector and also message server and all object in service condition, I attach as reference. Strange thing is, one 1 function block can be generate alarm, the other are can't ( we use PP library) . We also already check alarm condition on control builder, we found that on function block alarm conditions is disable, even though we already toggle it using faceplate and interaction windows, i attach reference for detailed. Why alarm condition is not activated ?Please give advise for this kind of problem?
I've been struggling to configure the alarm on 800xa System. System using 800xa Ver 6.0.2, controller using PM862, operating system using windows 10, system architecture just use 2 pc, 1 for EWS act as Engineering workstation, Aspect Server and Connectivity Server, second PC use for Operator works station. We already configure the Alarm Manager, Even Collector and also message server and all object in service condition, I attach as reference. Strange thing is, one 1 function block can be generate alarm, the other are can't ( we use PP library) . We also already check alarm condition on control builder, we found that on function block alarm conditions is disable, even though we already toggle it using faceplate and interaction windows, i attach reference for detailed. Why alarm condition is not activated ?Please give advise for this kind of problem?
Answers
1.Navigate to the Event Collector Service Group(OPC_AE_AC800M)
2.Select the Service Group Definition aspect in the Aspect List Area.
3.Select the Special Configuration tab in the Preview Area.
4.Select OPC AE Server for AC 800M in the Alarm Server drop-down list box.
5. Click Apply.
6.Verify that OPC AE Server for AC 800M is set in the Collection Definition
drop-down list box.
2.Select the Service Group Definition aspect in the Aspect List Area.
3.Select the Special Configuration tab in the Preview Area.
4.Select OPC AE Server for AC 800M in the Alarm Server drop-down list box.
5. Click Apply.
6.Verify that OPC AE Server for AC 800M is set in the Collection Definition
drop-down list box.
Here is probably your problem circled in red

CondState 0 = disabled in controller code, OR illegal settings.
Study the System Event List while downloading your application; likely you will see a system event "AlmDefErr xxx" indicating that the alarm block xxx have failed due to improper settings.
Here is what you need to avoid, for each alarm block:

CondState 0 = disabled in controller code, OR illegal settings.
Study the System Event List while downloading your application; likely you will see a system event "AlmDefErr xxx" indicating that the alarm block xxx have failed due to improper settings.
Here is what you need to avoid, for each alarm block:
- Too long source name or condition name
- Illegal characters in source name or condition name
- Not unique combination of source name + condition name
- Severity = 0
- Class = 0