Symphony Plus and AC800M Importer Tool
Hi everyone,
The AC800M Importer Tool includes in Symphony Plus SV 2.1 and 2.1.1 is not allowed to import tags and variables from "Diagrams", it is just available import tags from programas or single control module. Is there any options, tool or walkaround to solve this?
Thanks in advance.
César.
The AC800M Importer Tool includes in Symphony Plus SV 2.1 and 2.1.1 is not allowed to import tags and variables from "Diagrams", it is just available import tags from programas or single control module. Is there any options, tool or walkaround to solve this?
Thanks in advance.
César.
Answers
Hi,
If the tags and variables are not set to "hidden", then it gets exposed to OPC. So in that case, you can create tags manually in Symphony Plus and also update the dataprocessor for the object model. It will work.
If the tags and variables are not set to "hidden", then it gets exposed to OPC. So in that case, you can create tags manually in Symphony Plus and also update the dataprocessor for the object model. It will work.