FIO-11 RTD Connection
Dear All,
I want to connect 3RTD and Speed Ref. Signal to ACS880 Drive, so i added one "FIO-11" Module to the drive, for some reason, I need to connect the speed reference to AI1 , so i connect the RTDs as follows,
-the first RTD as shown in manual between AI2 & AO2
-the second RTD between the AI & AO of the extension module "FIO-11"
My question is, Can I connect the third one between AO1 on the drive and on AI2 on "FIO-11"?
Regards,
Abdelrazzaq Hiasat
I want to connect 3RTD and Speed Ref. Signal to ACS880 Drive, so i added one "FIO-11" Module to the drive, for some reason, I need to connect the speed reference to AI1 , so i connect the RTDs as follows,
-the first RTD as shown in manual between AI2 & AO2
-the second RTD between the AI & AO of the extension module "FIO-11"
My question is, Can I connect the third one between AO1 on the drive and on AI2 on "FIO-11"?
Regards,
Abdelrazzaq Hiasat
Voted best answer
Hi
I not have at this moment one drive ACS880 with the FIO-11 unit to test your configuration.
IMHO this could be possible, do not forget to configure the AO that you want to use as source for your temperature probe
I not have at this moment one drive ACS880 with the FIO-11 unit to test your configuration.
IMHO this could be possible, do not forget to configure the AO that you want to use as source for your temperature probe
Add new comment