800xA Multisystem Integration not working on Operator clients
Hi All,
I have configured Multisystem integration on 800xA 5.1 Rev C FP4 systems successfully and able to import structures from Remote Provider to subscriber.
However, graphics that are imported are not getting dynamized at the Operator clients. The graphics are working fine on the servers although.
I have valid licenses installed on Remote access subscriber system.
What could have went wrong?
Thanks
I have configured Multisystem integration on 800xA 5.1 Rev C FP4 systems successfully and able to import structures from Remote Provider to subscriber.
However, graphics that are imported are not getting dynamized at the Operator clients. The graphics are working fine on the servers although.
I have valid licenses installed on Remote access subscriber system.
What could have went wrong?
Thanks
Answers
If you have live MI-data on the subscriber system’s servers but not in its clients you might have a problem with affinity.
If you have deployed affinity on the subscriber system, verify that the RAC servers are part of the clients’ choice of servers for OPC DA Connector.
Hint: always maintain ”All nodes” in every affinity row, as a backdoor in case a server is missed out.
If you have deployed affinity on the subscriber system, verify that the RAC servers are part of the clients’ choice of servers for OPC DA Connector.
Hint: always maintain ”All nodes” in every affinity row, as a backdoor in case a server is missed out.
Add new comment